Crane 432 HC Error


Recommended Posts

I’m working on a Crane 432 that recently set the HC.ERR code.  Does the code disable the compressor & if so is there a way to clear the code that I’m overlooking. The compress won’t start by shutting the door, but the owner has told me that he was able to start the compressor (Assuming he bypassed some way) & it ran & cooled very well. 

Link to comment
Share on other sites

Opening and closing the main door should reset the health timer. Be aware that once the door is closed there is a 4-5 minute delay. Edited the compressor starts. You should be able to get the temp from the temp sensor. 

Link to comment
Share on other sites

2 minutes ago, cvending said:

Opening and closing the main door should reset the health timer. Be aware that once the door is closed there is a 4-5 minute delay. Edited the compressor starts. You should be able to get the temp from the temp sensor. 

Error isn’t clearing when the door shuts. I had assumed so on the delay, waited & hoped. Temp appeared to be showing correct, 72 degrees (room temp). 

Link to comment
Share on other sites