Daliab Posted June 6, 2015 Share Posted June 6, 2015 What's causing ice on the condenser Thermostat at 3. Located in an enclosed porch. Was empty two days ago loaded new so there's only a third full. Has been sitting for many many months without being used before I bought it. Product is cold. The old machine that this replaces didn't do it for 12 years. This is a new machine for me although it's a number of years old. Link to comment Share on other sites More sharing options...
orsd Posted June 6, 2015 Share Posted June 6, 2015 Low freon? Link to comment Share on other sites More sharing options...
SchligVend Posted June 6, 2015 Share Posted June 6, 2015 Is the fan running? Clogged drain? Link to comment Share on other sites More sharing options...
Daliab Posted June 6, 2015 Author Share Posted June 6, 2015 Fan is running. Drain is open. Frost/ice located in the top radiator type condenser inside behind and below product chute. In addition frost/ice located on the Copper bulb located in front of said condenser. I don't think the freon is low because when I was working on it in the garage for two weeks it would cool very quickly. I did start it after moving it around the house on a dolly and didn't wait 24 hours for the Freon to settle maybe that's the problem . Link to comment Share on other sites More sharing options...
AZVendor Posted June 6, 2015 Share Posted June 6, 2015 That is very likely due to low freon however, because you say the accumulator also is ice cold and frosty, you might have bad valves in the compressor. The accumulator should never be cold enough to ice up. You need to have someone check it out and if they know what they're doing they can tell you what's going on with it. Link to comment Share on other sites More sharing options...
KychrisKy Posted June 6, 2015 Share Posted June 6, 2015 Look at the fan make sure its running pretty fast, it could be going out n not running fast enough, make sure there's no open areas such as seals n door flaps etc Link to comment Share on other sites More sharing options...
Daliab Posted June 6, 2015 Author Share Posted June 6, 2015 the one icing up is the top one not the bottom one. Made sure door was closed tight... Not sure it was closed all of the way when I originally loaded the machine. Goofing to check tomorrow and see if it corrects itself. Link to comment Share on other sites More sharing options...
KychrisKy Posted June 6, 2015 Share Posted June 6, 2015 I wish u luck, this is a nickle n dime business we need to save as much as poss Link to comment Share on other sites More sharing options...
Daliab Posted June 18, 2015 Author Share Posted June 18, 2015 Replaced thermostat with a new one. Does the wire sensor go behind the evaporator or on front of the fan behind the evaporator ? Machine isn't icing up on the evaporator as bad as it use to but the compressor seems to run all of the time. I can turn off the thermostat and the compressor will turn off but the fan behind the evaporator will continue to run. I think this is normal. The product is cold. Can the freon be low even though the product is really cold at even on the lowest thermo setting? Link to comment Share on other sites More sharing options...
AZVendor Posted June 18, 2015 Share Posted June 18, 2015 You really need to put a thermometer in the machine to see what the temp is at. You should be at 38 to 42 degrees. What model machine is this as that makes a difference in where the capillary tube goes. And yes, the evaporator fan in the cabinet runs at all times. Link to comment Share on other sites More sharing options...
Daliab Posted June 18, 2015 Author Share Posted June 18, 2015 Dixie Narco 320/184-7. 36 degrees on thermostat setting 3 Link to comment Share on other sites More sharing options...
AZVendor Posted June 18, 2015 Share Posted June 18, 2015 On the older DN machines the cap tube should be one that's folded at the end which is then pushed into a tube that runs behind the evaporator from the right side. Turn the machine off when you try to slide it in there as there is 110v around the thermostat on that side. The thermostat should then be set to 3 1/2. Link to comment Share on other sites More sharing options...
Daliab Posted June 18, 2015 Author Share Posted June 18, 2015 Will have to check for a tube. I placed the folded end of the sensor wire behind the sheet metal directly behind the evaporator. Behind the sheet metal is a channel opening from the right which leads directly in front of the fan. One has to be careful because the wire can hit the fan blade because there is no guard keeping the wire from hitting the blade. Will go check for a tube. Link to comment Share on other sites More sharing options...
Daliab Posted June 18, 2015 Author Share Posted June 18, 2015 Found the tube... Would never looked for one if you didn't say something! Buttoned everything back up and made sure temp set a 3. Will see if compressor shuts off. Thanks AZVendor! Link to comment Share on other sites More sharing options...